CrabbyT
Structural
- Feb 12, 2019
- 165
I'm working on a job that involves the installation of a 150 HP - 200 HP pump for a new well and I'm trying to understand how the foundation should be designed. For centrifugal pumps, the rule of thumb is that the base should weigh at least 3x the equipment it supports.
Does anyone know if the rule of thumb applies for foundations that support vertical turbine pumps (i.e. well pumps)?
Can someone tell me what weights to consider? For example, I have the following:
[ul]
[li]Bowl weight = 1200 lb[/li]
[li]140' column pipe (10" i.d.) and shaft = 7000 lb[/li]
[li]140' of water inside the column pipe = 6800 lb[/li]
[li]Discharge head = 500 lb[/li]
[li]200 HP motor = 2500 lb[/li]
[li]TOTAL WT (not considering water) = 11200 LB[/li]
[/ul]
3x the total weight is 33600 lb, and now I'm looking at an 8'×8'×4' block of concrete. The problem is, this doesn't come close to reflecting any existing details I've come across. The existing details are more like 3'×3'×6'.
This leads me to believe that maybe I don't need to consider the weight of the column pipe and the shaft. Maybe those two things are heavy enough and long enough that they help to alleviate vibration. Problem is, I can't find any literature to support this.
Thoughts? In terms of vibration, am I only trying to restrain the 200 HP motor (2500 lb)? Or do I need to consider the total weight?
For soil bearing strength purposes, I'm including all the weights listed above (including the weight of the water).
Does anyone know if the rule of thumb applies for foundations that support vertical turbine pumps (i.e. well pumps)?
Can someone tell me what weights to consider? For example, I have the following:
[ul]
[li]Bowl weight = 1200 lb[/li]
[li]140' column pipe (10" i.d.) and shaft = 7000 lb[/li]
[li]140' of water inside the column pipe = 6800 lb[/li]
[li]Discharge head = 500 lb[/li]
[li]200 HP motor = 2500 lb[/li]
[li]TOTAL WT (not considering water) = 11200 LB[/li]
[/ul]
3x the total weight is 33600 lb, and now I'm looking at an 8'×8'×4' block of concrete. The problem is, this doesn't come close to reflecting any existing details I've come across. The existing details are more like 3'×3'×6'.
This leads me to believe that maybe I don't need to consider the weight of the column pipe and the shaft. Maybe those two things are heavy enough and long enough that they help to alleviate vibration. Problem is, I can't find any literature to support this.
Thoughts? In terms of vibration, am I only trying to restrain the 200 HP motor (2500 lb)? Or do I need to consider the total weight?
For soil bearing strength purposes, I'm including all the weights listed above (including the weight of the water).