ChrisConley
Mechanical
- May 13, 2002
- 975
Hello All,
I'm looking into the possibility of a variable primary flow chilled water system. I've heard all the warnings about minimum flow, but the client would still like to investigate. The system is a retrofit ~750tons, water-cooled chiller. We are replacing the existing chiller, cooling tower, primary pumps and condenser pumps.
My issue is that the secondary loops that feed off the primary loop are all pump driven coils with three-way mixing valves for capacity control.
What I would like to do is control the primary pump to run according to the number of secondary pumps that are operating.
Right now the existing system circulates 2400 gpm if even one small 80 gpm coil is calling for cooling. Please no comments on the flows as the original system was designed for a much larger load – a load they have yet to achieve in 40 years of operation. We will be reducing the primary flow to match the load profile and new chiller.
Has anyone ever controlled a pump VFD like this? Also, does anyone have any warnings about variable flow through the chiller beyond the standard? We are also considering variable speed on the chiller and/or the cooling tower.
I'm looking into the possibility of a variable primary flow chilled water system. I've heard all the warnings about minimum flow, but the client would still like to investigate. The system is a retrofit ~750tons, water-cooled chiller. We are replacing the existing chiller, cooling tower, primary pumps and condenser pumps.
My issue is that the secondary loops that feed off the primary loop are all pump driven coils with three-way mixing valves for capacity control.
What I would like to do is control the primary pump to run according to the number of secondary pumps that are operating.
Right now the existing system circulates 2400 gpm if even one small 80 gpm coil is calling for cooling. Please no comments on the flows as the original system was designed for a much larger load – a load they have yet to achieve in 40 years of operation. We will be reducing the primary flow to match the load profile and new chiller.
Has anyone ever controlled a pump VFD like this? Also, does anyone have any warnings about variable flow through the chiller beyond the standard? We are also considering variable speed on the chiller and/or the cooling tower.