ThePunisher
Electrical
- Nov 7, 2009
- 384
I am currently conducting an arc flash study and it also includes making arc flash labels associated with 4.16 kV isolation switches at the OUTPUT of VFDs.
I understand that when a fault occurs at the switch terminations (while switch is closed), the fault contributions would come from the VFD output (which would be limited to a maximum of 150~200% VFD FLA) and motor contribution (approx. Locked Rotor Current).
I would like to ask what would be a typical VFD clearing time or shutdown time when a short circuit occurs at the closed switch's terminals. I have difficulty getting this estimated from the VFD manual. I would think it should be as fast as a fuse as the VFD may have recognize a short circuit from an overload due to sudden voltage dip.
The VFD I am modeling is an ABB ACS1000i rated for 2,250 HP, 13.8-4.16 KV
Thank you to anyone who can support me.
I understand that when a fault occurs at the switch terminations (while switch is closed), the fault contributions would come from the VFD output (which would be limited to a maximum of 150~200% VFD FLA) and motor contribution (approx. Locked Rotor Current).
I would like to ask what would be a typical VFD clearing time or shutdown time when a short circuit occurs at the closed switch's terminals. I have difficulty getting this estimated from the VFD manual. I would think it should be as fast as a fuse as the VFD may have recognize a short circuit from an overload due to sudden voltage dip.
The VFD I am modeling is an ABB ACS1000i rated for 2,250 HP, 13.8-4.16 KV