VFD power cable shielding (screening) issues 1
jraef
I have been heavily promoting the use of VFD shielded power cable in my installations, and most of the problems I have experienced in the past have been diminishing to near extinction. But today, I went to a site with MULTIPLE motor failures connected to a VFD system that I designed, but was altered before purchase and installed by neanderthals. So in my investigation, I found that ALL of the repeated motor failures are happening in the exact same type of application, wherein they took the one single drive I had put into an MCC, and used it to run 4 smaller motors (12A drive running 4 motors that are 2.7A each) on evaporator coils in a cold room. The motors are supposedly "inverter duty" (but I find that is often about as reliable as a fox telling the farmer that the chickens are safe), I could not see the actual motors. So at first glance it SHOULD have been OK in theory. They did install a Load Reactor on each drive, then they used VFD shielded cable, one that has 3 power leads, 3 symmetrical ground leads nested in them, an overall braided shield over those 6 and a separate EGC (Electrical Grounding Conductor, a term used in the US similar to a "PE" conductor). The typical linear distance from MCC to evaporator set is between 300 and 400 ft, through open cable tray. The VFDs did not show faults in the fault logs, other than Power Loss faults typical of being powered down from opening the MCC cubicle doors.
The only big problem I can find with the installation is that the neanderthal electricians just routed the cables haphazardly (as in a bowl of spaghetti) in cable tray along with other full voltage motor leads and the incoming power leads, and then when they ran the shielded cable to the motors, they cut and taped off the shields at the motor connection box end, so they are shielded only at the VFD end. The motor lead cable goes from the MCC to a fiberglass box on the side of each evaporator, and inside is a local disconnect switch, a power splitter block, and a ground bar, to which the EGC is attached, along with 14ga ground wires from the motors. Motor leads from this box to the motors themselves are NOT shielded any longer, they used what appears to be non-shielded flexible wire through gland fittings on the box. I always tell people to ground both ends of shields on POWER cables, because the intent is to form a sort of Faraday cage. But what does / could happen if only one end is grounded? Could this possibly explain the multiple motor failures?
More relevant info:
(1) The motor re-winder that has repaired these has told the user that the motors are failing on "single phasing", which makes no sense to me. The VFDs in question should trip out on loss (or severe imbalance) of output phase current. I have provided the end user with EASA photos of typical single phase motor failures and typical turn-to-turn insulation failures due to standing waves, they have yet to share that with the re-winder to confirm his findings.
(2) To my horror, the user deliberately CHOSE to remove the separate Manual Motor Starters at the evaporators which were to be protecting the individual motors. So there is NO realistic motor overload protection for these 2.7A motors, other than the OL setting of the VFD, which is set at 10.8A. I have told my contact on the job site that this violates the NEC, but the decision came from a manager, so he said he does not want to challenge him and has asked that my report de-emphasize that issue (not likely). Still, these are evaporator coil fans, it is virtually impossible to overload them, and they are only 3 months old so no time for normal bearing wear. While I was there today the VFDs were at 55-60Hz and the 4 motors were drawing only 4.5 - 4.8A collectively for all 4 motors.
My theories at this point are:
1) The lack of shield grounding at one end rendered the shield ineffective, so standing wave generation caused first-turn insulation failure, which the motor re-winder was unfamiliar with and misidentified as single phase damage.
2) The lack of shielding is causing rapid bearing EDM damage and failure, which causes the motors to overload, which again, the re-winder misidentified as damage from single phasing.
3) None of this has any importance whatsoever, and all of it was just caused by the neanderthals who did the motor hookups likely not making good connections at the splitter blocks. Still, I would have expected the VFD to trip on that though.
Please share your thoughts.
"Will work for (the memory of) salami"
Dedham Community Theatre!
Home of Museum of Bad Art - Art, too bad to be ignored!
Been there twice. Love the Place.
Gunnar Englund
Follow up, mainly to share the knowledge in case something like this comes up again:
5 months later, they repaired all of the shield connections, made up missing ground connections, cleaned up the wiring, everything I told them to do. We sent a field tech out to the site who scoped everything, no problems found, no voltage spikes seen, good ground continuity throughout. Clean, normal, good.
20 more motors have failed... I feel like I'm in the twilight zone here.
The motors, Baldor "Inverter Duty", have been sent to Baldor corporate (as opposed to local shops), they came back and said the failures are consistent with first turn insulation breakdown due to reflected wave phenomenon...
Per my suggestion, the user installed what we call "Motor Terminators", basically a self-contained RC snubber system that you mount near the motor to absorb the spikes if they happen. Since then, no more motor failures, but it hasn't been long yet, only about a week for the last installs. But... now the Load Reactors in the VFD cubicles are overheating and the insulation on THEM is failing, but only on the units in which the distance from drive to load is right around 250 ft!
The consensus now, from a large sampling of power quality gurus within my company, is that it might be a rarely seen phenomenon in which the reactors act in resonance with the cable capacitance to actually create reflected wave voltages, and since nobody has ever added the terminator down stream of a load reactor (because there would be no point), the phenomenon is exacerbated but the effect is only seen at the reactor end. Can't explain exactly why, but we're going to tell them to remove (jump out) the reactors on those units and see if the motor failures cease.
"You measure the size of the accomplishment by the obstacles you had to overcome to reach your goals" -- Booker T. Washington
Jeff,
I think that the whole situation could benefit from real world measurements instead of consensus in a "large sampling of power quality gurus within your company".
Excuse me, but PQ gurus seldom have a clue about what can happen between motor, cable, VFD and other components that have been installed or added. Have those gurus produced anything else than consensus? A failure model with verified data so you can do some basic calculations?
Have any measurements been made? With calibrated and compensated probes that 1) can withstand the voltage and 2) whose band-width isn't degraded by a "protection resistor" that some of the very large companies tell their field guys to use. And, further, have those measurements been made directly between motor terminals (which is a bad idea because of the capacitance from scope GND to real world GND that exists even in the best battery operated scopes) or have the measurements been made terminal to GND in differential mode (the only reliable way to do that measurement if an insulation amplifier isn't used)?
The fact that the load reactors are overheating points to resonance between reactor and cable and that resonance often is in the 10+ kHz range, which turns the coil into an inductive oven that heats the core. Are there any damping resistors parallel to the reactors? If not, you need to add them.
The terminators (RC combinations) that I have tested usually never worked. My recipe is thus:
1. Find out what the motor terminal voltage actually is and compare rise-time and peak voltage to the manufacturer's limit.
2. Check the reactor/cable system for ringing. Add damping resistors parallel to the reactors until the ringing is gone.
3. If necessary: Add common-mode filters. Not measly ferrite cores, they are not very useful. Use nanocrystalline cores. They are, in my experience, the only ones that help.
Excuse my rant, but when I hear about 20 motors that have failed - I can't shut up. This is, after all, what I do most of my time.
Gunnar Englund
Yes it was scoped, yes, the engineer we sent out there claims that he knew what he was doing (I grilled him personally based on feedback from in here), he found nothing indicative of the failures we are seeing. The highest voltage peak he recorded was 1426V, the motor insulation is supposed to be 2000V. The only thing different about his testing is that because the motors are embedded inside of the evaporative coolers which are on trapezes hanging from the ceiling, he cannot get to the individual motor connection boxes, the cooler must be disassembled for that. So he took his measurements at the common connection box where the 4 motors on each unit all connect to the cable coming from the VFD, the next to last photo above. The longest distance from that box to the motor is about 5ft at most.
What about ringing? Did he notice any?
Gunnar Englund
Sinewave filters are the solution that I would apply to this if it happened here. Problem is cost and physical space, but it will overcome the problems.
Bridging out the reactors could cause issues with the capacitive current overloading the IGBTs and causing VFD failures.
I think Gunnar is probably right (as usual) and there will be some high frequency ringing. I have seen it a number of times, and also been told that there is none because the scope has too low a bandwidth, or the operator is not looking at the HF components. Power quality type scopes usually just don't cut it for this type of investigation.
Becoming an expensive exercise, glad I am not in the firing line for paying the costs!!
Best regards,
Mark.
Mark Empson
Advanced Motor Control Ltd