VFD Sensitivity to Line-Side Frequency Variations

Status
Not open for further replies.

EddyWirbelstrom

Electrical
Feb 17, 2002
215
Does VFD load-side frequency remain constant when the line-side frequency changes by say +/- 10% ?
 
Replies continue below

Recommended for you

Yes. The incoming AC is only used to make DC so as long as the voltage is up to spec, the input frequency could easily vary over +/- 10% without problems.

In fact, most drives built for the world market are dual-rated for 50/60hz.
 