In response to a closed thread inquiring to water heater setpoint: My rule of thumb for storage type water heater temperature setpoint depends on the use of the hot water.
Setpoint should be 140 deg F with master mix down or point of use mix down to 115-120 deg F.
Exception: Small systems with no showers can have setpoint at 120 deg F, except in medical facilities.
Reason: Legionella is a bacteria that is most commonly acquired through inhalation. If there are no showers and the system is small, then there is little chance for the inhalation of Legionella if somehow it manages to form in the system. However, there is always a chance of Legionella forming in temperatures 140 and below.
Setpoint should be 140 deg F with master mix down or point of use mix down to 115-120 deg F.
Exception: Small systems with no showers can have setpoint at 120 deg F, except in medical facilities.
Reason: Legionella is a bacteria that is most commonly acquired through inhalation. If there are no showers and the system is small, then there is little chance for the inhalation of Legionella if somehow it manages to form in the system. However, there is always a chance of Legionella forming in temperatures 140 and below.