Hi,
I have a pump sizing task at hand and want some expert opinion. Pumps have to supply domestic water from an underground water tank (ugwt) of 237,266 gal. to 2 overhead water tanks (ohwt) each of capacity 39,688 gal. meaning in total approx. 79,000 gal. According to UPC, total water supply demand is 650 gpm. Adding roughly irrigation and factor of safety I take it to be 700 gpm. According to my understanding of the water supply demand calculated from UPC, it already includes diversity factor. Therefore, we can say that the ohwt will be emptied in 79,000/700 = 113 mins. Therefore, I have to supply water in these tanks at a greater rate so that the feeding pump (from ugwt to ohwt) does not run continuously.
1. If I select 3 pumps of 1250 gpm each to run in sequencing (through electronic controls), each pump will run for approx. 1 hour in every 6 hours so the duty cycle will be 1/6 = 16.67% (I am not sure on this duty cycle terminology..correct me if I am wrong). Is this approach fine? or I need to change something?
2. Building is approx. 150' high. A 74 psi head pump will be fine? Secondly, I plan on supplying water to ohwt using 8in dia. PPR pipe. Is it an optimum choice? It gives the velocity as 10ft/sec and friction loss approx. 1.5 psi/100 ft from "Fairly Smooth" chart of UPC (chart A 105.1(2)). I wish to use 6in pipe but that would give me a higher velocity and friction loss as well or i have to reduce the flow from 1250 gpm.
3. Lastly, due to the smaller capacity of the ugwt as well as ohwt (architect is not allowing them to be bigger), I plan on using 60,000 gallons in ugwt for firefighting purposes using fire pumps as the building is partially sprinklered and dedicate ohwt to domestic water use only. I will have to use a booster pump for the top most floor to make pressure at fixtures greater than 8psi and use pressure reducing valves at lower floors to keep it lower than 80 psi. What do you say? Am I missing anything?
Thanks to all of you for the help you are going to give!
I have a pump sizing task at hand and want some expert opinion. Pumps have to supply domestic water from an underground water tank (ugwt) of 237,266 gal. to 2 overhead water tanks (ohwt) each of capacity 39,688 gal. meaning in total approx. 79,000 gal. According to UPC, total water supply demand is 650 gpm. Adding roughly irrigation and factor of safety I take it to be 700 gpm. According to my understanding of the water supply demand calculated from UPC, it already includes diversity factor. Therefore, we can say that the ohwt will be emptied in 79,000/700 = 113 mins. Therefore, I have to supply water in these tanks at a greater rate so that the feeding pump (from ugwt to ohwt) does not run continuously.
1. If I select 3 pumps of 1250 gpm each to run in sequencing (through electronic controls), each pump will run for approx. 1 hour in every 6 hours so the duty cycle will be 1/6 = 16.67% (I am not sure on this duty cycle terminology..correct me if I am wrong). Is this approach fine? or I need to change something?
2. Building is approx. 150' high. A 74 psi head pump will be fine? Secondly, I plan on supplying water to ohwt using 8in dia. PPR pipe. Is it an optimum choice? It gives the velocity as 10ft/sec and friction loss approx. 1.5 psi/100 ft from "Fairly Smooth" chart of UPC (chart A 105.1(2)). I wish to use 6in pipe but that would give me a higher velocity and friction loss as well or i have to reduce the flow from 1250 gpm.
3. Lastly, due to the smaller capacity of the ugwt as well as ohwt (architect is not allowing them to be bigger), I plan on using 60,000 gallons in ugwt for firefighting purposes using fire pumps as the building is partially sprinklered and dedicate ohwt to domestic water use only. I will have to use a booster pump for the top most floor to make pressure at fixtures greater than 8psi and use pressure reducing valves at lower floors to keep it lower than 80 psi. What do you say? Am I missing anything?
Thanks to all of you for the help you are going to give!