We are doing maintenance on our VCP breakers and have heard some extra 'sizzling', more than normal when racking out breakers. We then opened the shutters with the breaker out of the cell, turned off the lights and were able to see partial discharge occurring on the line side of the stabs. There is a a metal cover over the Poly barrier that fit over the metal stabs individually.
I hope the picture populates for reference. The metal is super thin and the only reason I would think for this assembly would be for the mounting bolts that hold the Poly barrier in place, and when you torque down on them it won't crush the poly barrier. Anyhow, the discharge is happening on the the small tabs and am wondering if anyone has come across this issue. I am sure over time we will incur more of an issue with breakdown and tracking. I appreciate your time.