What is the best method of drilling tangent piles in loose clay which would ensure the bore stability?
 
Replies continue below

Recommended for you

What are tangent piles? Like a secant piles wall? And typically you would say soft clay not loose. Loose is for granular soils

CFA is the most economical as it doesn’t require casing. A bored pile would in soft clay
 
Sounds like some form of concrete pile, right. If soft and caving some form of cased pile likely needed, but an augured pile using hollow stem augers and grout them pumped as auger is withdrawn is done also. Trade names given to them, such as Franki, Prepakt.
 
Perhaps you can also consider deep soil mixing (soil-cement columns).
 
EireChch,
Tangent piles touch, secant piles overlap.
 
Hokie66 is right about tangent piles.

@EireChch, yes, I meant soft clay, with 1-3 SPT blow counts. Did you mean a bored pile would collapse in soft clay? even with the use of bentonite slurry?

Actually we had a project of this nature and when the excavation was done, the quality was not good. I am posting some pictures and would ask for some insight into the reasons, the solutions and the possible rectifications of the quality issues.
IMG_3061_f5de5l.jpg
IMG_6562_lgeljb.jpg
IMG_6561_dursoj.jpg
IMG_6563_p5kp7i.jpg
IMG_3062_qb4cuc.jpg
IMG_6564_w2twhu.jpg
IMG_0560_j5rtah.jpg
 
Go9lly,what do you expect? I think you might have had a little better setting the machine, but these pictures would make me satisfied as to the job, considering placement of the rig.
 
Those pictures show an unsatisfactory installation, IMHO. This is a case for placing concrete under slurry.
 
Your "tangent" piles wall has certainly been constructed with a CFA rig. You have what you paid for : low cost job. If you want a "nice" wall then go for secant piles, either cased CFA or cased rotary. This will ensure verticality good position of piles. One problem with soft clays is that you need a minimum cohesion of 15 kPa. If you don't have this minimum value, soil will not provide enough lateral support for fresh concrete pressure. This may lead to non complying piles and as a minimum to large concrete overbreaks.
 
Exactly as BigHarvey notes- with clays that soft, extrusion of the grout into the confining material is inevitable. Cased bored piles would be ideal for maintaining pile form...no client ever wants to pay for them but I'd say from the limited information available that your ground conditions justify them.

Watch out for pile communication if you're going with a tangent wall.

All the best,
Mike
 
Is there any reason why driven piles would not be suitable?
 
@ BigHarvey, This wasn't a CFA rig. It was the conventional hydraulic straight rotary; IMT 180 and SoilMec SR60. the drilling was done with the help of bentonite slurry to stabilise the borehole.

@Oldestguy, I wouldn't say the placement of the rig. Actually the kelly guide of both rig were removed for some reason. In my opinion, the issues in alignment were due to this. The architect was surely worried with the results, because he lost some space of the basement.

@Hokie66, I agree with you. But I want to know how can we have better results and what precautions are to be taken when pouring concrete in slurry?

@MadMike @BigHarvey, The communication between the piles is also an issue. When we install the temporary casing, it has to have a diameter more than the pile diameter. So, we actually cannot get a tangent pile if we install a guide casing, and if we do, as in our case, the casing cuts the adjacent piles and damages the reinforcement as well if we lose the verticality. We proposed a secant pile system, but the structural engineer didn't agree.
If the soil do not have a minimum 15KPa cohesion, even if we case the piles, when we remove the casing, will the soil be able to provide the lateral support?

@LRJ, I haven't seen anyone use driven piles as earth retaining structures.
 
if the clay is that soft, I'd consider deep soil mixing with inserted H-piles. We did this in hydraulic fill and it enabled wales with tiebacks as we dug down to grade.

f-d

ípapß gordo ainÆt no madre flaca!
 
Pile déviations are very important for a rotary pile, hence my comment on CFA. Anyway don't use tangent piles. You should also, if not done use guide walls to position accurately the piles and control verticality. Casing the full length of the pile will help you for verticality because of the rigidity of the temporary casing.
If the clay shows less than 15 kPa of cohesion you can press statically concrete sheetpiles in the ground, it's commonly done in Bogota (Colombia).
You can also use CSM (Cutter Soil Mixing) and steel beams to construct a temporary retaining structure.
 
I think you should immediately design DSM in the places where piles are seperated. One by one. Three secant DSM with a triangular shape would stop the water. However, I can't see any water? Why did you choose tangent piles?
 
There is water at 17' below NGL. The total excavation is 21'. Dewaterting wells are installed to lower the water table. The design was of the consultant. We recommended secant instead but the consultant was rigid.
 