What is typical switchgear DC control power voltage in Germany? 1

Status
Not open for further replies.

xnuke

Electrical
May 3, 1999
1,029
I realize this question is somewhat customer-specific, but what are people seeing a lot of customers using?
24 V DC?
48 V DC?
125 V DC?
250 V DC?
Other?




xnuke
"Live and act within the limit of your knowledge and keep expanding it to the limit of your life." Ayn Rand, Atlas Shrugged.
Please see FAQ731-376 for tips on how to make the best use of Eng-Tips.
 
Replies continue below

Recommended for you

Check the applicable standards.
IEC 61439 (-2, I think) for low voltage switchgear
IEC 62271 (-2 as well, I believe) for high voltage switchgear.

You will likely find that the at some output level, the control power voltage value changes.

Converting energy to motion for more than half a century
 
we have a lot of German equipment on site:

LV control- 24V DC
HV control-110V DC with battery back up (10x 12V batteries)
 