I am interested in getting some opinions from other PE's on a deflection/cracking problem on a recently constructed residence. I am the SE of record for a $3 million residence in an area with high snow loads (85psf). The design was mostly performed by a junior structural engineer and reviewed and stamped by me.
There is a 20 ft long ceiling joist span on a 2/12 roof that is framed with with wood I-joists designed with a deflection of L/470 snow load and L/380 total load deflection with SL=85psf and DL=20psf. (IBC limit is L/240 for snow load on roof members). The rafters are perpendicular to the roof slope. There is a glulam beam in the ceiling with points of support (walls below) that cause it to deflect very little. The purpose of the glulam is for perpendicular roof framing for a 4 foot roof overhang. The calculated L/380 deflection of the adjacent I-joists is about 0.63" and a crack has developed in the drywall seam that I believe has been caused by the differential deflection of the I-joist vs. the glulam.
We were contracted by the Architect to perform the structural engineering for this project. The architect has basically told the owner that it isn't his problem. The owner called me and I am going to meet him at the house this week to take a look at the problem.
I am interested in getting others' opinions on this situation. Who do you think should be responsible? Engineer, architect, or contractor? On one hand, maybe I should have required L/1000 deflection...on the other hand that is really not practical or cost effective for most structural designs and this is a situation that I have never encountered before.
On a side note: The owner is an attorney and from the questions he was asking on the phone I felt like I was already on the witness stand. He surely will not go quietly and I can understand...I wouldn't want ceiling cracks in my new home either.
There is a 20 ft long ceiling joist span on a 2/12 roof that is framed with with wood I-joists designed with a deflection of L/470 snow load and L/380 total load deflection with SL=85psf and DL=20psf. (IBC limit is L/240 for snow load on roof members). The rafters are perpendicular to the roof slope. There is a glulam beam in the ceiling with points of support (walls below) that cause it to deflect very little. The purpose of the glulam is for perpendicular roof framing for a 4 foot roof overhang. The calculated L/380 deflection of the adjacent I-joists is about 0.63" and a crack has developed in the drywall seam that I believe has been caused by the differential deflection of the I-joist vs. the glulam.
We were contracted by the Architect to perform the structural engineering for this project. The architect has basically told the owner that it isn't his problem. The owner called me and I am going to meet him at the house this week to take a look at the problem.
I am interested in getting others' opinions on this situation. Who do you think should be responsible? Engineer, architect, or contractor? On one hand, maybe I should have required L/1000 deflection...on the other hand that is really not practical or cost effective for most structural designs and this is a situation that I have never encountered before.
On a side note: The owner is an attorney and from the questions he was asking on the phone I felt like I was already on the witness stand. He surely will not go quietly and I can understand...I wouldn't want ceiling cracks in my new home either.