Who makes a 345kV power voltage transformer?
pcwebb
Needed for station service at remote substation;
50kVA
Primary voltage 345kV
Secondary voltage- 120/240VAC
Accuracy of 0.3%ZZ or better
"Station Service" and 0.3%ZZ don't usually go together. Is this for metering or station service power?
Check ABB. Or Google "high voltage instrument transformers".
pcwebb-
No one to my knowledge (and I work for an instrument transformer company in the US) makes PVT's above 230 kV. At 345 kV about the best you're going t oget is a VT with a thermal burden of about 10 kVA at most. We have sold some in 3-phase sets to deliver a 3-phase power of 30 kVA.
To DPC's question, it is possible to have a PVT with a metering winding. The metering winding can be set to be accurate at full load (i.e. when the PVT is supplying station power) or it can be set to be accurate when the PVT is not supplying station power. A typical application is to have the PVT as a back-up source for station power, in which it is used under normal conditions for metering/protect, and in the event of loss of primary station power, it can step and provide needed power. Of course, under this arrangement it will not deliver metering accuracy when used for station power.
ABB got out of PVTs in the US when they closed their plant in Bloomington, IN. They are really on in instrument transformers now up to 34.5 kV in the US.
scott,
What about Trench? (not in US, I realize). Also, doesn't ABB still do HV PTs outside of US?
dpc
DPC-
I'm pretty sure Trench does not. You can check with them, but I'm about 99.9% sure they don't. I work for Ritz (now part of Areva) and we are only 1 of 2 companies that go up to 230 kV for PVTs for the North American market.
Yes...ABB still has HV IT's outside of the US. I believe they produce in Sweden, in addition to other factories around the world.
pcwebb,
Check with Kuhlman. They are making station service transformers that have a high primary voltage for applications that are remote. Don't know if they can get the accuracy you need though.
Check this, I know they do.
Legal Name: Pauwels Canada Inc.
Operating Name: Pauwels Canada Inc.
Mailing Address
101 Rockman St.
WINNIPEG, Manitoba
R3T 0L7
Location Address
101 Rockman St.
WINNIPEG, Manitoba
R3T 0L7
Website URL:
jmmee97-
I believe Kuhlman only goes up to 230 kV. You can check though.
scottf,
Checked with Kuhlman. Only up to 230kV.
Hey wait a minute. Isn't 345 kV the L-L voltage? And why would anyone have a L-L connected station service transformer?
If 345 kV is indeed the L-L voltage, the L-G voltage is 199 kV, within range of Kuhlman's 230 kV limit.
All units are rated based on their system voltage. A 230 kV unit is the L-L voltage.
Trench will quote a 345kV, SF6 Insulated, 50kVA, 120/240V, +/- 3%, estimated $90-100K
Made in Germany
Thanks for your comments
pcwebb-
First I've ever heard of an SF6 PVT. I'm surprised they can meet the temperature rise requirement with SF6 insulation.
You might want to see a type test report (I would hopefully make the same recommendation if I wasn't a competitor, so take it with a grain of salt :)