Transformer differential protection will operate for LL and LG faults within transfomer, then y we need a additional REF protection for star connected winding, in addition there is another neutral overcurrent relay,
 
Replies continue below

Recommended for you

REF is more sensitive for a ground fault low in the winding. REF protection is included in most modern transformer protection relays at no extra charge. If you have a neutral CT, there is not cost for the additional protection.
 
What Jghrist say.
In additional, if your grounding is resistance or compensated, REF is storngly recommended function.
Best Regards.
Slava
 
Hi,

87T doesn't cover 100% of the star winding, this is why we add REF to cover 100% of the star winding in case of L-G faults.

thanx
SMB
 