- Mar 28, 2005
- 2
I hope this is in the right place. If not, please advise or move it.
My previous background has been Control Systems/PLC's etc. I am now involved in a project involving 4 each 4000 HP motors which will pull about 560 amps at 4160 VAC 3 phase 60 Hz.
On a previous similar project, the motors were 3 each 1000 HP at 4160 V, pulling about 140 amps each. Incoming line voltage is 25 KV.
I think the 4000 HP design is going to require individual transformers from 25 KV to 4160. My first concern was wire sizing. For this kind of current, the NEC tables (at least the way I interpret them) tell me that 1000 MCM cable has an ampacity of about 700 or so amps.
Should I instead be considering busways for additional current capacity? Should I lobby for higher voltage motors thus reducing the current, and try to design for single transformers to handle the entire 16,000 HP load? Either way, the size (and cost) is starting to get VERY LARGE to my thinking.
BTW the local utility is also putting restrictions on voltage flicker (3% max), and harmonics per IEEE 519. The voltage flicker means that softstart or reduced voltage start is going to be a must in this case.
Any thoughts out there???
My previous background has been Control Systems/PLC's etc. I am now involved in a project involving 4 each 4000 HP motors which will pull about 560 amps at 4160 VAC 3 phase 60 Hz.
On a previous similar project, the motors were 3 each 1000 HP at 4160 V, pulling about 140 amps each. Incoming line voltage is 25 KV.
I think the 4000 HP design is going to require individual transformers from 25 KV to 4160. My first concern was wire sizing. For this kind of current, the NEC tables (at least the way I interpret them) tell me that 1000 MCM cable has an ampacity of about 700 or so amps.
Should I instead be considering busways for additional current capacity? Should I lobby for higher voltage motors thus reducing the current, and try to design for single transformers to handle the entire 16,000 HP load? Either way, the size (and cost) is starting to get VERY LARGE to my thinking.
BTW the local utility is also putting restrictions on voltage flicker (3% max), and harmonics per IEEE 519. The voltage flicker means that softstart or reduced voltage start is going to be a must in this case.
Any thoughts out there???