Dracula7
Industrial
- Nov 2, 2012
- 18
Hi,
Could anyone help me understand why this is a 277V configuration across the heaters instead of 480V? The incoming power is 480V, delta - so no neutral, while the heaters are 277V, single phase. My guess is that you can get 277V from a 480V only between phase and neutral -which is not the case here since there's no neutral. I attached here a hand draw wiring with 2 heaters in parallel per phase and just one heater per phase.
Thanks all in advance!
Could anyone help me understand why this is a 277V configuration across the heaters instead of 480V? The incoming power is 480V, delta - so no neutral, while the heaters are 277V, single phase. My guess is that you can get 277V from a 480V only between phase and neutral -which is not the case here since there's no neutral. I attached here a hand draw wiring with 2 heaters in parallel per phase and just one heater per phase.
Thanks all in advance!