Larf03
Electrical
- May 29, 2006
- 9
I have a common sytem using dry contacts for level monitoring and the dry contacts send signals to two machines. I have wired the input on the same contact i.e: Input 13 of machine 1 is wired to the same contact as Input 13 of machine 2. When both machines are powered up, everything works fine but when I shut down power feed to one machine, the inputs are activated even if the contacts are not closed.
There is obviously a leak from input card of machine 1 to input card of machine 2 up to the power supply of machine two (wich acts as a resistive circuit when power is down). I work with 24 volts supply and when the problem occure, I read 13 volts at the contact wich is supposed to feed the input)
I have tried putting a diode on the input card's commom pin but it doesn't work. I really need a solution because the whole goal of this common system was to have one unit running while the other one was serviced and still be able to monitor the level application
There is obviously a leak from input card of machine 1 to input card of machine 2 up to the power supply of machine two (wich acts as a resistive circuit when power is down). I work with 24 volts supply and when the problem occure, I read 13 volts at the contact wich is supposed to feed the input)
I have tried putting a diode on the input card's commom pin but it doesn't work. I really need a solution because the whole goal of this common system was to have one unit running while the other one was serviced and still be able to monitor the level application