Jonskelton

Electrical
Nov 19, 2022
7
Evening all

I’ve got a 2.6kw induction motor, inside the motor cap I’ve got 12 terminals, the machine it came off had a 2 speed setting, all the cables went back to a multipole switch for 1450 or 2800. I’m trying to use the motor from a single phase in 3 phase out VFD.
Tested the motor out and I seem to have 6 pairs all with about equal resistances, my question is 1 is it possible to run this motor delta for use on the VFD, 2 - how best can I identify which pairs I need to use to wire delta for use with my VFD

THANKS
 
 https://files.engineering.com/getfile.aspx?folder=b1f92dd3-7437-4a98-99dc-26c9f7b7b370&file=FB847AA9-A9A4-4C24-9EBC-88BC495D8FD0.jpeg
Replies continue below

Recommended for you

If it's a 2 speed motor then it will have two independent sets of windings. That would naturally have 6 leads. The fact that yours has 12 leads me to believe it has a high/low voltage option as well. Pairs will be wired in series or parallel depending on input voltage. Identify the windings for the high speed and connect those to your VFD. Tape off the remaining connections.

A picture of the nameplate will get you a more accurate answer.
 
How could I identify either of the speeds? For delta I’ll just need to connect the end of one to the end of another power it, other end connected to another pair end, power it and so on?
 
The information you need is typically on the nameplate of the motor or on the inside of the cover for the junction box.

Is the motor still connected to the multi-pole switch? Find the 3 leads connected to the high speed terminals on the multi-pole switch. Those are the 3 leads you need to connect to your VFD.
 
There was 6 connections going to the multipole switch
 
0376437B-9FC8-47B5-BF48-1F1DFD38279F_pz0ayg.jpg
 
The motor does not appear to be 2 speed or dual voltage from the nameplate. That is strange.
 
Some people will use the 12 lead configuration to indirectly attain 2 speeds, by using a Wye-Delta or Part Winding arrangement but not solely as a starting scheme, they leave it in the first stage as the low. So really it is two TORQUES, then the load determines the speed that it runs at with the lower torque. This however only works with centrifugal machines like pumps and fans.

To use it with a VFD, just connect it for the voltage that you are running at, the VFD will take care of the rest (with proper programming of course).


" We are all here on earth to help others; what on earth the others are here for I don't know." -- W. H. Auden
 
With all the terminals unmarked in the motor cap, how could I identify which is which? I can tell with my ohm meter which ones pair up but I’m left with 6 pairs. Which ones would go together ?
 
With 1:2 speed, it's a Dahlander winding as below.

Delta is low speed (supply at 1U 1V 1W and 2U 2V 2W open).

Two Wye is high speed (supply at 2U 2V 2W and 1U 1V 1W shorted).

Tricky part is identifying the leads if they are not marked.


Dahlander_xgltm1.svg


Muthu
 
TugboatEng it’s not connected to the switch at the moment but I have marked where all the cables were connected to.

Edison123 if I was to connect it in a fashion which I think is delta according to your diagram, if it was wrong would it not spin at all? I can try it on a true 3 phase supply as I’m dubious about connecting it to the VFD if I’ve got it wrong
 
Since you have marked the leads, restore the original connections to the multi speed switch, apply direct voltage without VFD as before to check the both the speeds and then insert the VFD between the supply and the switch.

Muthu
 
I haven’t got 3 phase here also I need to wire it in delta before the single to 3 phase inverter will work
 

Then you need to take it to a winding shop where they will most likely suggest to rewind it for your speed and connection since it a major pita to sort out 12 unmarked leads. Or buy a new motor for your specs.



Muthu
 
Actually you don't.
There is no way to tell if a motor is internally connected wye or delta from the supply wires. The inverter cannot tell a wye motor from a delta motor.
I once had to connect a consequent pole (Dahlander) motor with all the markings missing.
I removed the rotor and with a battery and a compass I identified each winding location and polarity by energizing a winding and then finding the physical location and polarity with the compass.
What is your supply voltage?

--------------------
Ohm's law
Not just a good idea;
It's the LAW!
 