Wood Gusset Connected Trusses

Status
Not open for further replies.

medeek

Structural
Mar 16, 2013
1,104
I've done some work analyzing and programming a truss calculator for MPC wood trusses however I've put that project on hold and I'm not looking at trusses made with plywood gussets. I'm not finding a significant amount of information online regarding these types of trusses. Does anyone have any links or even books they could recommend. I would like to create a truss calculator for this type of truss that is similar to the previous calculator I started working on, however this time I will incorporate the wind and snow load cases as well as engineer the gusset plates (ring shank nails and glue).
 
Replies continue below

Recommended for you

About 40 years back, we did a lot of northern Hudson Bay stores in northern Canada with wood trusses... we used a Cremona diagram to analyze them by drafting and the connections used 1/2" D.Fir plywood gussets. The fasteners used were Stelco hardened spiral truss gusset nails (8ga x 2-1/2" long, I think). I seem to recall we used a capacity of 250 lb/nail, which was very high and they were driven from alternate sides.

CMHC used to have a manual and they had prescribed designs for roof trusses, also. I'll try to upload a file... having problems with it for some reason...

Dik
 
It seems like the Canadians have done a lot more with wood gussets than their neighbors to the south. I'm trying to determine the specs on the special hardened spiraal concrete nails that were used on these plans.

Another point of confusion for me after some further study of the NDS is with plywood. The NDS rates the strength of plywood not by its thickness but rather by the number of plies and by the span rating. What I would like to know is DF EXP1 STRUCTURAL 1 15/32 or 1/2 readily available and can I get it in 5 ply with a span rating of 32/16 or 24/0?
 
After doing my requisite homework (remember I am still quite new to the structural field) I've determined that for double shear I have 4 yield limit equations for the fastener checks at each joint. I'm some previous posts I've seen comments about assigning a certain lateral force per fastener, this seems a whole lot simpler than running a bunch of calculations. Where did these simpler allowable load per nail come from?
 
Factored lateral resistance for various nails and various penetrations are given in the Wood Design Manual printed by the Canadian Wood Council. The values are based on the most critical failure mode given in the code.

BA
 
After running a few numbers for 10d nails into 15/32 DF Structural 1 plywood (5 ply) with DF truss members it looks like the 10d nails don't have as much capacity as I originally thought. In particular I'm looking at the splice joint in the bottom chord with a pure tensile load of approx. 1800 lbs. It looks like I'll need at least 10 nails on each side in double shear. However the plywood itself is the weak link, 3-1/2 deep gusset on each side of the bottom chord will not be enough for this tensile load. The load is D + S so my Cd is 1.15, which buys me a little but not much.
 
Not sure what you mean by a 10d nail. The diameter seems to be different depending on which chart you look at. On the attached chart, the diameter is 0.148" and the length is 3". Is that what you are using? If so, you will be clinching the nails.


Are you using DF truss members? In my area, SPF is more common and much easier to work with for nailing.

It is not necessary for the gusset plate to be 3.5" deep. Make it deeper if required for the sloping chord member.

BA
 
Check publications from University of Virginia. They are big on this stuff. I built my first house and many garages with the system you are looking at, but I always used ring shank nails, With the modern nail guns you can add plenty more than your numbers call for to be sure. Clinching not needed and most nails won't go much beyond the 2 inch members. Thus, call that extra length as added, not computed for , strength.
 
Using 1/2" plywood gussets, the overall width of two gussets and a 1 1/2" member is 2 1/2". According to our code, you can use 2 1/2" nails in double shear provided that nails are alternately driven from each side. Alternatively, you can use 3" nails driven from either side and clinched. Nail capacities and minimum spacing are stipulated in our code and presumably also in other timber codes.

BA
 
I think I've figure it out but we will see. I'm working on the code right now to calculate everything. I'll be using the AWC NDS 2012 and the ANSI TPI 1-2007 where applicable. Once I get something together I'll post it and let everyone take a look at it. My hope is that it will help take some of the guess work out of designing wood gusset connected trusses, not just for myself, but others as well.
 
Here is a fairly good articles on plywood/OSB gussets for 2x wood trusses. As for the size of nails I prefer to use 8d (or 6d) common nails from each face, with 1/2 gussets. The 8d will penetrate both gussets which I feel will add strength if from each face similar to clinching. Of course you can not use the double value for the calculations. Adding glue to the high stress members like BAretired stated also helps.

Garth Dreger PE - AZ Phoenix area
As EOR's we should take the responsibility to design our structures to support the components we allow in our design per that industry standards.
 
 http://files.engineering.com/getfile.aspx?folder=d56515e9-2efe-4b18-9947-f2b6c267d697&file=Repair_of_Wood-Trusses-Fox-Nov-08.pdf
Now that I think I have the fastener portion figured out I'm now looking at the failure modes of the plywood gusset plates themselves in tension and in shear. ANSI TPI 1-2007 describes the critical dimension as the gross width of the plate measured parallel to the joint line (section 8.4.3 and 8.5.3). What I've drawn below are these gross widths for tension and shear for each joint.

Wp1web.jpg


Wp2web.jpg


I am trying to consider all failure modes. In particular Joint (3) has possibly 3 failure modes but tensile case 2 and tensile case 3 may be redundant.
 
Off the top, your joint 7 has too many nails to the horizontal member. Connection force only has to be for the force difference in the web members, not the summation of the forces.

Dik
 
Nails are cheap. Piece of mind is not. The number of nails for that bottom chord does not really change the plate size. So you might as well fill the space you've got.
 
I bet the engineering time spent on this would outweigh the cost of a proper metal plate connected wood truss design
 
manstrom,

In most cases you may be right, but there may be situations where pre-fabricated trusses cannot be delivered to the site on time.

BA
 
You are correct manstrom. The engineering costs for a one off of this type of truss is too high forcing most ranchers, farmers and DIY'ers to just wing it and forgo the engineering. I'm trying to create a program that automates the engineering of this type of truss so that it is affordable to do the engineering. I do have some experience with MPC trusses and I have done this sort of thing before, look at:

Medeek Truss Designer

However, I've never looked at plywood gusset plates before so I'm in uncharted territory.

Last night I spent some time rereading certain sections of the ANSI TPI 1-2007 and I now think I have a rational approach for dealing with the additional lateral forces on the fasteners due to moments at the peak joint and splice joints.
 
Sorry the link above should have been:

Medeek Truss Designer

To help get this project off the ground I'm listing it at Kickstarter (anyone had any experience with them doing a similar thing?).

Kickstarter Project

I've had some of my engineering friends baulk at this approach to engineering however I think more and more automation of engineering through software is the future of this profession. Most practicing engineers are already half way there since we all use Excel spreadsheets for most of our mundane and typical calculations. I'm just trying to take it a few steps further as it relates to wood gusset connected trusses.
 
Why not just add plywood gussets to your program (with some CYA notes) with the plywood tension/shear and nails holding values per a psi of plywood? After all an engineer should be reviewing and sealing any engineered design.

Garth Dreger PE - AZ Phoenix area
As EOR's we should take the responsibility to design our structures to support the components we allow in our design per that industry standards.
 