Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations cowski on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Wood Specific Gravity Adjustment Factor

Status
Not open for further replies.

Archie264

Structural
Aug 29, 2012
993
I can't find the reference for the darn thing. I'm probably looking right past it but I can't find it. I'm referring to the [1 - (.5 - G)] provision. Does anyone know the reference offhand, by chance? Thanks.
 
Replies continue below

Recommended for you

Look in the 2008 Edotion of AWC SDPWS-2008. For Wood Framed Diaphragms it is found under footnote 2 of Table 4.2A on page 18. For Wood Framed Shearwalls it is footnote 2 of Table 4.3A on 31.

The specific gravities of various wood species is found in NDS-2012, Table 11.3.3A on page 81.
 
Indeed, there it is! Thank you very much.
 