I have a question with regards to wind loading on a wall stud.
When designing a wall stud for out of plane wind loading, I always assume a Component & Cladding wind load along with gravity loads (Dead & Roof Live) for the roof with the revelant load combinations (i.e. D+W, D+0.75(Lr+W)).
For some reason, people in my office have been neglecting considering a positive wind load on the roof in addition to the wind load on the wall, which would increase the axial load in the stud.
My question is, if I were to start considering wind load on the wall and on the roof in the design of the stud, would I use Components & Cladding loads for both pressures. It seems too conservative to take C+C loads to design an element that is receiving that load from two surfaces. C+C loads represent the maximum intensity that can be expected over a small area. It seems very unlikely that could happen on both a wall and a roof at the same time. This idea is based what I learned from a professor at my school that is on the ASCE7 wind loading committee. He seems to like the idea of the summarily dismissing anything that collects load from two surfaces as MWFRS.
When designing a wall stud for out of plane wind loading, I always assume a Component & Cladding wind load along with gravity loads (Dead & Roof Live) for the roof with the revelant load combinations (i.e. D+W, D+0.75(Lr+W)).
For some reason, people in my office have been neglecting considering a positive wind load on the roof in addition to the wind load on the wall, which would increase the axial load in the stud.
My question is, if I were to start considering wind load on the wall and on the roof in the design of the stud, would I use Components & Cladding loads for both pressures. It seems too conservative to take C+C loads to design an element that is receiving that load from two surfaces. C+C loads represent the maximum intensity that can be expected over a small area. It seems very unlikely that could happen on both a wall and a roof at the same time. This idea is based what I learned from a professor at my school that is on the ASCE7 wind loading committee. He seems to like the idea of the summarily dismissing anything that collects load from two surfaces as MWFRS.