I'm performing some calculations for a substation and have been presented with the following system information at the point of connection:
3ph fault (5.53kA phase & positive sequence), X1/R1=4.8, R1=0.016pu, X1=0.077pu
2ph-G fault (6.75kA, 6.99kA phase), (3.2kA, 4.4kA, 1.2KA, zero, pos, neg) X1/R1=4.8, R1=0.016pu, X1=0.077pu, X0/R0=45, R0=0.0007pu, X0=0.031pu
1ph-G fault (6.94kA phase), 2.31kA (sequence: pos=neg=zero), X1/R1=4.8, R1=0.016pu, X1=0.077pu, X0/R0=45, R0=0.0007pu, X0=0.031pu
My question is, do I use the positive sequence impedance X/R ratio (4.8) or the zero sequence X/R ratio (45) for decrement factor calculations such as IEEE80 section 15.10, IEEE605 Equation 18.
Do I only use the zero sequence value for earth faults, and all other faults use the positive sequence value? 45 seems very high for a zero sequence X/R ratio...
Thanks in advance