- May 8, 2006
- 11
I frequently need 120 volt delta power. It's always temporary for about a week and loads very from 1 to 30 kW. I usually simulate this by re-wiring a 480 volt delta to 208Y/120 transformer so that the primary is Y with the neutral ungrounded. I end up with 69 volts to ground on my grounded Y neutral conductor in the secondary, but the 120 phase-to-phase is right. A Square D engineer once told me this was OK (I ended up with him because I was trying to buy a 120 volt delta transformer and no one at the sales level even understood what that was). After reading posts to this site, I thought I should ask for a second opinion. If this sounds dumb, notice the 'mechanical' next to my name. Your comments appreciated.
Steve