Zero sequence impedance of cable

Status
Not open for further replies.

JakeLong

Electrical
Jun 23, 2023
4
0
0
DK
I'm trying to calculate the zero sequence impedance of a cable for the calculation of single phase to ground fault and could use some clarification.

The cable in question is 3x300/25mm² NA2XS2Y 6/10(12)kV, which there will be installed two of in parallel along with a 35mm² PE conductor.

Is it right to assume Z0 = Z1 + 3*Ze, where Ze is only the impedance of the PE conductor. Or should the impedances of the metallic screen and earth be included in the calculation, as a parallel impedance?

 
Replies continue below

Recommended for you

@wcaseyharman unfortunately this is not the case here, but the document @7anoter4 linked does say it is better to consult with the cable manufacturer on this matter, which I will give a go. Thanks for your answers.

Though if they give me the Z0-value of the cable, won't this value only apply to the shield and earth values? How should the impedance of the PE conductor then be modeled into the Z0-value?

 