@PMR06 - Ref ASCE 7-05, Refer to Figure 6-6 for calculating external pressure coefficients Cp for walls (windward, leeward, and side wall) and roofs (windward and leeward) of all heights, for MWFRS purposes. For roofs, the external pressure coefficient would depend on the distance from windward edge as given on page 49. The design wind pressure on the walls and the roof would be combination of external + internal pressures.
After getting design wind pressures on the walls and the roofs using Fig 6-6 for each of the directions X and Y, do combinations of wind loads using cases 3 & 4 of Fig 6-9. These combinations are applicable to both, the walls and the roof.