Considerng bond strength with anchorage resistance length and lapping length.

Status
Not open for further replies.

Gnoowij

Civil/Environmental
Nov 7, 2023
5
Dear all,

There is two rebar in a row with lapping length, 100mm.
Anchorage_lapping_qxxigm.png

In case that I cannot follow the standard length of anchorage length and lapping length of rebars, can I consider the as the following?
(lapping length is considered as anchorage length)

Tension force = 300kN
Rebar
a) Dia : D20
b) fbd = 3Mpa
c) Anchorage length : 300mm
d) lapping length : 100mm
e) Total anchorage length = 400mm

=> F, (Rebar resist agaist tension) = fbd x L(300+100) x Perimetre of rebar = 377kN
 
Replies continue below

Recommended for you

No, you cannot. Anchorage and lapping to embedded bars are not capacities that can be combined. You must develop enough capacity in one or the other.

In this case, your anchored bar will attempt to pass force into the D20 embedded bar. The lap length is not adequate to transfer that force, so the concrete between those two bars will locally overstress. After that, the anchored bar will attempt to pass the force into the concrete as a basic anchorage problem. The concrete will create a tension breakout cone (around 200kN).
 