Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations cowski on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Recent content by MSUK90

  1. MSUK90

    small span RC Zig-Zag beam design

    As suggested by BAretired, just consider a flat slab spanning between columns and analyse and design accordingly.. Have done this numerous times. No idea of a rough/accurate analysis of zig-zag beams.. I would consider two cantilever beams supporting the central beam if beams need to be used(the...
  2. MSUK90

    Baseplate (with axial & moment) on unreinforced slab on grade

    StrEng007, can you share more data for the same? Like magnitude of compression force, uplift and moment? What type of structure is it? Etc.. Also, I have rarely seen an unreinforced slab on grade. Generally they provide a wire mesh here for every grade slab.
  3. MSUK90

    Blockwork on steel beam

    Is it possible to plant some concrete columns(200mmx200mm-4T12 longitudinal reinforcement with minimum required ties) at say 3m spacing? The column rebar should be be welded to steel beam. The wall will then be laterally supported by columns which will be supported by steel beams?
  4. MSUK90

    Column-Isolated Footing joint

    HTURKAK, Thanks for sharing the document. I have read the section 5.5. I still have concern why a base SHOULDN'T be assumed fixed if every service and ultimate limit state is satisfied(even if the soil is weak)? Secondly, lets say a steel column is resting on a pedestal which is supported by an...
  5. MSUK90

    Column-Isolated Footing joint

    HTURKAK, Thanks for the response. The link you have shared isn't showing any data in my browser.
  6. MSUK90

    New foundations next to existing ones

    niboo_boss, can you draw a section between the old and proposed foundation as per your design proposal? I want to have a look.. KootK, thanks for this detailed explanation. Personally, I always try to look for some solution which doesn't have any connection to the existing structure; don't know...
  7. MSUK90

    Column-Isolated Footing joint

    I have seen typical details as shown in figures (a) and (b) shared by HTURKAK. And I also have seen many engineers say that a footing can not be considered fixed if the soil condition is poor. However, I believe that if we check a footing(soil) for all serviceability checks, then there is no...
  8. MSUK90

    New foundations next to existing ones

    KootK, how do we achieve option 2b suggested by you at site? And wouldn't tying the new footing to the old one will overload the old footings?
  9. MSUK90

    Column-Isolated Footing joint

    jimstructures, I think OP is asking regarding the connection detail between the concrete pedestal/column and footing joint if connection is assumed pinned.
  10. MSUK90

    Concrete Column Lateral Deflection Check for Industrial Sheds

    Thanks a lot for your inputs SlideRuleEra and human909. Why is it so?
  11. MSUK90

    Raft with stand down beams

    Spot on! Also, regarding the uplift from swelling clays, I have never encountered that situation until now in my career. Would Love to design with its consideration once.
  12. MSUK90

    Raft with stand down beams

    Most probably from SOIL?
  13. MSUK90

    Concrete Column Lateral Deflection Check for Industrial Sheds

    1) The columns, beside roofing, will support walls all along the edges of shed and I don't think a lateral deflection of 70mm is anyhow accepted for concrete block walls. 2) I don't think so. 3) May be, May be not, I am not sure as no one has ever complained about that in past. I have to depend...
  14. MSUK90

    Concrete Column Lateral Deflection Check for Industrial Sheds

    Its a general question, varies from project to project. Lets say for example, I get deflections of around 70mm for 400mmx400mm columns. Total height of column being around 7m. If I check allowable limit by H/500, it will be around 14mm.