thanks for the reply. Yes it is stand alone building. it is part of another building (that is on the design phase at this time). what if the building is sprinkled? can i have a different zone for the cold storage with deluge system? i think this situation will be on the rule that "if the build...
What if i have an elongated room. with an area of 517 sq.ft. its classified as light hazard. in light hazard the sprinkler have 225 sq.ft of protection so, 517/225 = 2.297
use: 3 sprinkler in the room. but since its elongated should i use 6 sprinkler to protect the room? the dimension of the...
the roof construction will be GI sheet. is has insulation i think its not combustible. but the space have access and the FCU will be place in that space. will this affect the protection of the building? and please help me site and code that describe my situation i been reading 8.15.1 Concealed...
i have a question, is it required to put sprinklers below the roof? the situation will be an existing warehouse will be converted to an office building. there is a space [highlight #204A87]between the roof and the ceiling (just like an attic). thanks,
Good day! i have a situation that seems very easy for you guys. how can i reduce ambient temperature inside a room using ventilation system alone. For example, my target ambient temperature drop is (-5 degrees Celsius) in a closed room using outside air.
Example data:
Outside air: 40 degrees...
For the lights, i can consider it surface mounted since it is mounted on a electrical tray like support with the fans and other utilities. im talking about standard spray sprinkler (pendent type sprinkler), im reading NFPA 13. i have read already about ESFR and CMSA it was stated that light are...
Im trying hard to find a code that states that lighting fixture is considered as an obstruction to our sprinkler. Is there any code state that? Please direct me.thanks
Can someone please confirm if im using the correct way of sizing up a chilled water pipe? the total TR of all the fan coil unit is 40 TR. 40TRx 2.4GPM = 96GPM
then i input it into the sizer it said im should us3 80mm size pipe. my other question is, how can i size up the pipes in their max...
The owner wants the EE room to be ventilated. just to remove the heat coming from the panel boards. the total load of all the panel boards is 336.22 kVa. 5% of the total load will be 16.811 kVA. i calculated 172 cfm for the estimated heat dissipation. i not just sure of the Delta T (F) since the...
i used 10ACH in the room with 796 sq.m volume. i have no data regarding the heat dissipation of a panel boards. how can i calculate the heat dissipation?
what air change can i use to ventilate a electrical rooms where 7 panel boards are installed inside? i was able to find 4-6 air change. can i use this air change? thanks
can anyone teach me how to size the bellmouth if i have 20000cfm supply air? i read the size of bellmouth should be double the size of the main return duct so that the return air will have low velocity in the ceiling. thanks