BentEng
Structural
- Jan 15, 2018
- 19
Hi all,
Looking at the CL 14.6.7 requirement for "all horizontal lapped bars within the central two-thirds region of the wall shall be provided with minimum 135degree hooks and lapped with a full-strength splice (figure 14.6.7(D).
1. What is the central two-thirds region? Is this meant to be the middle third region?
2. If lapping outside of this zone, but not in the boundary element, is a standard lap acceptable?
3. Why is this detail necessary, when CL14.6.6 already dictates the design shear to be increased to the (full) elastic shear force. If treating the walls as non-ductile, the shear force is possibly the same as limited ductility, but not the detailing. Further, if the wind shear force is greater than the full, elastic seismic shear force, would the hooked detailing still apply?
4. Is a "full-strength splice" just a tension lap splice? The term "full-strength splice" isn't used anywhere else on the code that I can see.
Appreciate any thoughts or help on this.
Looking at the CL 14.6.7 requirement for "all horizontal lapped bars within the central two-thirds region of the wall shall be provided with minimum 135degree hooks and lapped with a full-strength splice (figure 14.6.7(D).
1. What is the central two-thirds region? Is this meant to be the middle third region?
2. If lapping outside of this zone, but not in the boundary element, is a standard lap acceptable?
3. Why is this detail necessary, when CL14.6.6 already dictates the design shear to be increased to the (full) elastic shear force. If treating the walls as non-ductile, the shear force is possibly the same as limited ductility, but not the detailing. Further, if the wind shear force is greater than the full, elastic seismic shear force, would the hooked detailing still apply?
4. Is a "full-strength splice" just a tension lap splice? The term "full-strength splice" isn't used anywhere else on the code that I can see.
Appreciate any thoughts or help on this.