I am looking through the ASCE 7-10 requirements for leeward snow drift on adjacent (lower) structures (horizontal separation s less than 20'), and it appears there is a significant difference in the approach from ASCE7-05 to 7-10. To summarize, per 7-05 drifts were applied to all adjacent structures (within 20') with lower roofs, but this drift could be reduced by the factor (20-s)/20 where s is the separation distance. Per ASCE 7-10, buildings within the aerodynamic shade region receive drift with some limitations on drift height for buildings relatively close in height.
This all appears to make sense, but can have a very large impact for buildings nearing the 20' limit. Basically, based on 7-10, for a building with 19.5' separation from a taller building (h>s/6) the roof must be designed for a full leeward drift from the fetch of the taller structure. This is not reduced based on the separation distance. The same building with a 20.5' separation does not have to designed for any drifting snow from the taller building.
Per ASCE7-05 the drift would have been reduced based on the size of the separation to a very small percentage of the full leeward drift.
Making things even more confusing is that if the low roof continues over to the the high roof (no separation) the same portion of roof we were referring to does not have to be designed for any drift.
See attached sketches for clarity.
Am I missing something here? I get that drift is complicated and hard to predict, but I am having a hard time telling a client that we must design a roof for 100 psf drift loads unless we adjust the separation by 1 additional foot (in which case there are no significant drift loads required).
This all appears to make sense, but can have a very large impact for buildings nearing the 20' limit. Basically, based on 7-10, for a building with 19.5' separation from a taller building (h>s/6) the roof must be designed for a full leeward drift from the fetch of the taller structure. This is not reduced based on the separation distance. The same building with a 20.5' separation does not have to designed for any drifting snow from the taller building.
Per ASCE7-05 the drift would have been reduced based on the size of the separation to a very small percentage of the full leeward drift.
Making things even more confusing is that if the low roof continues over to the the high roof (no separation) the same portion of roof we were referring to does not have to be designed for any drift.
See attached sketches for clarity.
Am I missing something here? I get that drift is complicated and hard to predict, but I am having a hard time telling a client that we must design a roof for 100 psf drift loads unless we adjust the separation by 1 additional foot (in which case there are no significant drift loads required).