BubbaJ
Structural
- Mar 18, 2005
- 163
I have a project where there is an anticipated 170 psf suction force on a roof topping slab. The purpose of the slab is to protect the roofing below it. #3 ties were provided in a 6'x5' grid to anchor the slab to the precast double tee roof structure.
A series of unfortunate events for the contractor has resulted in a slab w/o the required reinforcing and the wrong fiber additive.
In lieu of tearing the slab off and starting over, the contractor has come up with the attached detail. They want to drill in new #3 "within an inch or two" of the existing #3. If the two slabs are adequately tied together, the resulting factored suction force is 118 psf or 3540# of hold-down force required per exist #3 tie.
I can't see how there will be adequate force transfer from the new #3 to the existing #3 to prevent the topping slab from becoming airborne during a 300 mph wind event.
Opinions anyone? (We can't drill new anchors into the dbl tees as we don't want to perf the vapor barrier that is below the insulation.)
A series of unfortunate events for the contractor has resulted in a slab w/o the required reinforcing and the wrong fiber additive.
In lieu of tearing the slab off and starting over, the contractor has come up with the attached detail. They want to drill in new #3 "within an inch or two" of the existing #3. If the two slabs are adequately tied together, the resulting factored suction force is 118 psf or 3540# of hold-down force required per exist #3 tie.
I can't see how there will be adequate force transfer from the new #3 to the existing #3 to prevent the topping slab from becoming airborne during a 300 mph wind event.
Opinions anyone? (We can't drill new anchors into the dbl tees as we don't want to perf the vapor barrier that is below the insulation.)