As you know, in Protection system we usually use close and Trip relay between Main relay (as commander) and circuit breaker.
These relays must have to main features, Heavy duty and high speed.
The main use of these relays is that, when main relays (for example Distance relay) sends trip to CB, about 4ampere are used by inductor of CB.
hen the relay contact wants to break this current ,it must withstand Ldi\dt voltage . this voltage usually results to destroy main relay contact.
So, based on this philosophy which above mentioned, we use trip and close relay.
After improvement in CB mechanism, the CB contact position is used in the path of relay and CB coil. So the trip current is broken by this contact (for example after CB is tripped, the CB will be opened, so the CB contact will be opened and breaks the trip current)
But we still use trip relay and close relay between main relay and CB,,why?
---------
For example we use 7PA27 Siemens relay as Trip relay and 7PA23 Siemens relay as Close relay.
I know just one reason.
These relays must have to main features, Heavy duty and high speed.
The main use of these relays is that, when main relays (for example Distance relay) sends trip to CB, about 4ampere are used by inductor of CB.
hen the relay contact wants to break this current ,it must withstand Ldi\dt voltage . this voltage usually results to destroy main relay contact.
So, based on this philosophy which above mentioned, we use trip and close relay.
After improvement in CB mechanism, the CB contact position is used in the path of relay and CB coil. So the trip current is broken by this contact (for example after CB is tripped, the CB will be opened, so the CB contact will be opened and breaks the trip current)
But we still use trip relay and close relay between main relay and CB,,why?
---------
For example we use 7PA27 Siemens relay as Trip relay and 7PA23 Siemens relay as Close relay.
I know just one reason.