cpiedra23
Structural
- Dec 8, 2012
- 16
hey guys.
please see attached detail.
i'm checking the CMU wall anchorage for out of plan loads per ASCE 7-10, Sect. 12.11.2.1
i thought i should check the hook development length "ldh" into the concrete per ACI 318-11, Sect. 12.5.2, and the #5 dowel for shear friction per ACI 318-11, Sect. 11.6.4. they both seem fine.
for the CMU, i was going to check the development length "ld" in the CMU per ACI 530-11, Sect. 2.1.7.3.
some questions:
1) the conc hook development length is mentioned for hooks in tension. similarly, the cmu development length is mentioned for tension. i don't have tension in these dowels but only shear. are these sections still applicable? do i get a reduction for shear only?
2) is there a similar 'shear friction' section for cmu? is this a necessary check?
any thoughts would be greatly appreciated. thanks!
please see attached detail.
i'm checking the CMU wall anchorage for out of plan loads per ASCE 7-10, Sect. 12.11.2.1
i thought i should check the hook development length "ldh" into the concrete per ACI 318-11, Sect. 12.5.2, and the #5 dowel for shear friction per ACI 318-11, Sect. 11.6.4. they both seem fine.
for the CMU, i was going to check the development length "ld" in the CMU per ACI 530-11, Sect. 2.1.7.3.
some questions:
1) the conc hook development length is mentioned for hooks in tension. similarly, the cmu development length is mentioned for tension. i don't have tension in these dowels but only shear. are these sections still applicable? do i get a reduction for shear only?
2) is there a similar 'shear friction' section for cmu? is this a necessary check?
any thoughts would be greatly appreciated. thanks!