GaStruct
Structural
- May 20, 2024
- 70
Hi All,
Long time reader, first time posting.
I have a client that wants to extend his 6" concrete basement wall 2'-0" to increase the ceiling height and re-grade his yard (the house has been demolished to the foundation).
How would you go about dealing with this hinge? The required embedment to lap and to develop a post installed #4 bar is about 30". Hilti only allows a 5" embedment for a 6" wall with HY-200 adhesive! My only thought would be to reduce the capacity by the ratio of 5/30 and see if that is greater than the applied forces (should be small this high up).
It just feels crazy to not try to get this to work as underpinning also creates a hinge even lower on the wall but that gets done semi-frequently. No way dowels are getting embedded the required length.
Let me know your thoughts. Rough sketch is attached.
Long time reader, first time posting.
I have a client that wants to extend his 6" concrete basement wall 2'-0" to increase the ceiling height and re-grade his yard (the house has been demolished to the foundation).
How would you go about dealing with this hinge? The required embedment to lap and to develop a post installed #4 bar is about 30". Hilti only allows a 5" embedment for a 6" wall with HY-200 adhesive! My only thought would be to reduce the capacity by the ratio of 5/30 and see if that is greater than the applied forces (should be small this high up).