NewbieStruct
Structural
- May 31, 2011
- 101
We were showing a 24"x24" x 2'0 tall concrete pedestal supporting a steel column (gravity) on our plans. The contractor has poured it incorrectly. It is about 12" off. In such cases, is it advisable to tear down the pedestal and construct a new one , or construct a new one by its side (12x24) and attach to the existing using epoxy dowels.