marinaman
Structural
- Mar 28, 2009
- 195
I've got a long concrete wall that I have designed. Every 32' the wall is "bumped" to the inside of the building to create a concrete pilaster to support a steel column above.
My question is in regards to the horizontal wall reinforcing. In my detail, I continue the horizontal wall reinforcing, for both faces of the wall, thru the integral pilaster. I just received the rebar shop drawings and he is terminating the inside face horizontal bars, at each pilaster, via a 90 degree hook.
I have designed these pilasters as integral with the wall....to be poured at the same time. Cast as one monolithic piece.
I have never had a detailer detail this like this before. I have always passed the horizontal bars thru the pilaster with no issue. There is not a bar conflict issue....as the closed ties of the pilasters are spaced amply to allow passage of the wall reinforcing thru the pilaster cage.
I realize that my detail will take more effort...but....the pilasters are integral with the wall and are designed as such. I pulled my CRSI information I have here in the office and do not see any example where CRSI recommends detailing as is shown in these shop drawings.
How do you guys detail your horizontal wall bars as they approach an integral, monolithic, pilaster?
My question is in regards to the horizontal wall reinforcing. In my detail, I continue the horizontal wall reinforcing, for both faces of the wall, thru the integral pilaster. I just received the rebar shop drawings and he is terminating the inside face horizontal bars, at each pilaster, via a 90 degree hook.
I have designed these pilasters as integral with the wall....to be poured at the same time. Cast as one monolithic piece.
I have never had a detailer detail this like this before. I have always passed the horizontal bars thru the pilaster with no issue. There is not a bar conflict issue....as the closed ties of the pilasters are spaced amply to allow passage of the wall reinforcing thru the pilaster cage.
I realize that my detail will take more effort...but....the pilasters are integral with the wall and are designed as such. I pulled my CRSI information I have here in the office and do not see any example where CRSI recommends detailing as is shown in these shop drawings.
How do you guys detail your horizontal wall bars as they approach an integral, monolithic, pilaster?