Hello all,
This is a hypothetical situation:
I have three #4/0AWG type-W 90C copper single-conductors installed an uncovered cable tray per 392.10. Cables are terminated to a transformer at one end and a breaker with 75C lugs on the other end. Ambient temperature worst case is 40C.
The base ampacity of the cable is 405A per table 310.17. Due to ambient temperature the cable is derated to 405A x 0.91 = 368.55A. Due to 392.11(B)(2) we have to derate by 0.65 so 368.55 x 0.65 = 239.55 which is about 240A.
Per NEC 110.14(C) I must determine the ampacity of the termination based upon NEC table 310.16. The base ampacity of a #4/0 termination at 75C is 230A. Multiplying by the derating factor of 0.88 gives me 202.4.
So in this situation the conductors have a rated ampacity of 240A while the terminations are rated 202A. Therefore, the ampacity of the circuit (ie. terminations and conductors) are rated for the lower of the two which is 202A.
I've been searching around and reading the NEC and UL standards all day now, and I was wondering if any of you guys can tell me if I am doing this right or wrong and/or offer any tips or links to some good reference material?
This is a hypothetical situation:
I have three #4/0AWG type-W 90C copper single-conductors installed an uncovered cable tray per 392.10. Cables are terminated to a transformer at one end and a breaker with 75C lugs on the other end. Ambient temperature worst case is 40C.
The base ampacity of the cable is 405A per table 310.17. Due to ambient temperature the cable is derated to 405A x 0.91 = 368.55A. Due to 392.11(B)(2) we have to derate by 0.65 so 368.55 x 0.65 = 239.55 which is about 240A.
Per NEC 110.14(C) I must determine the ampacity of the termination based upon NEC table 310.16. The base ampacity of a #4/0 termination at 75C is 230A. Multiplying by the derating factor of 0.88 gives me 202.4.
So in this situation the conductors have a rated ampacity of 240A while the terminations are rated 202A. Therefore, the ampacity of the circuit (ie. terminations and conductors) are rated for the lower of the two which is 202A.
I've been searching around and reading the NEC and UL standards all day now, and I was wondering if any of you guys can tell me if I am doing this right or wrong and/or offer any tips or links to some good reference material?