Hi,
As per API RP 553 (Refinery Valves and Accessories for Control and Safety Instrumented System) Clause 10.2.1 Control valves maybe used for depressurising service.
I have never came across a control valve being used for depressurising service. I have seen a general arrangement of a BDV (Blow Down Valve) along with a RO (Restriction Orifice), with a minimum distance of 600mm or 1000 mm between them to avoid cold creep to the BDV.
Have any of you have used/seen a control valve for depressurising service?
If yes, then what is the criteria for the same.
Thanks in advance.
Dinesh S SHELATKAR.
Process Engineer