Deck Ledger/Point Load 1

Status
Not open for further replies.

bigwaterbill

Materials
Aug 17, 2004
5
I have a 2nd story deck hung by 3 beams on metal hangers ( 10'apart) attached to a 2"x10"x20'ledger bolted (2-1/2" bolts & nuts @16"o.c.)through dbl. 2"x10" blocking between each joist. At 50lb.psf the outer beams (2-2"x10") at the hanger ledger connection would have a max. load of 1500lb. and the center beam (4-2"x10") 3000 lb. Is this ledger strong enough for these point loads.

All comments appreciated.
 
Replies continue below

Recommended for you

If I understand your description properly, the weak link is the shear connection of your blocking to the joists. Further, I don't understand how you attached two thicknesses of 2x lumber with a 2-1/2" bolt.
 
The bolts are 8"x1/2" two every 16"o.c. Pardon my previous description.
The blocking rests on sill plate of foundation (walkout basement). Blocking is nailed with 3-16d nails through each side of the floor joists into the ends of each side of the blocks.
What remedial action can I take to add to the shear connection if needed?
 
Add angle plates at each blocking.
 