Abby,
When you say you would put the kitchen on its own system, you mean that you would provide a make-up air unit for the kitchen that would both heat and cool? The unit would have humidity control, correct? Humidistat mounted where?
I've seen some kitchen MUAHUs designed for a minimum discharge air temp. of 60 - what is your experience with this and does it lead to humidity complaints?
Anyone else have any insight?
I am in a year round cooling environment. I typically would supply un tempered make up air probably 60 to 70% of what the hood exhausts through a back supply plenum.
The kitchen will have its own cooling system and perhaps this system draws in some fresh air as well, and makes up some of the remianing 30% of the exhaust air but not all of it.
The dining room system will have a fair amount of fresh air in it to ventilate for all the people. The fresh air in the dining room system also replaces what is exhausted out of washrooms. Because the kitchen is still running at a slight imbalance, air from the dining room will travel to the kitchen, and this movement of air tends to keep odors in the kitchen and out of the dining room.
You can sometimes have a gas fired unit to temper up the make up air in the winter and perhaps this air is introduced through ceiling diffusers and the kitchen basically heats itself.
Dependeing on where you live perhaps the make up air unit could have an evaporative cooling section on it, or even a DX coil, and then you would be conditioning all the make up air and using it to attempt to keep the kitchewn cool. It is economical if it works, with the evaporative cooler, perhaps it wastes a lot of energy with the DX option.
If it was a small facility, and the hood was say not much more than 6 feet long, sometimes I have used one unit for both the dining area and the kitchen but you do not want to be drawing return air from the kitchen. The make up air volume supplied at the hood is reduced and all the make up air is brought in through the HVAC.
You have no return from the kitchen, the air is exhausted up the hood.