gurse
Electrical
- Jun 27, 2019
- 17
I have a 7.5 kW motor with 110V, 40W anti condensation heater. But i have only 240 V supply for the heater, can I put a resistor in series with the heater to reduce the voltage please.
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
yes. average is not relevant to power calculations. rms is.Perhaps Average verse RMS is the fly-in-the-oinment?
please look at the true rms of the input and output voltages (all I saw for output was dc, which again is irrelevant for power calculations)The first test was with Fluke digital true RMS meters,
I agree.edison123 said:May be you can do the test and post the results here
2-star zlatkodo said:For a half wave rectifier Vdc = 0.45Vrms = 240 * 0.45 = 108 V DC
Using a simplistic analysis. 40W @ 110V does become 190W @ 240VAC. But, you're not applying the power 1/2 the time, you are applying the voltage 1/2 of the time which leads to applying the current 1/2 of the time which means the average power gets reduced to 1/4.
This does not correspond to the rms value of the half wave rectifier output.Half Wave Rectified DC
Vrms = Vp/(2*SQRT(2))
I think you put your finger on the intuitively appealing trap that people might fall into. The mean of the hwr signal is half the mean absolute value of the sinusoid. But of course none of the steps for computing the rms of a signal involves the mean of that signal (it's only the square of the signal whose mean is computed)with thoughts of applying voltage half the time being the same as applying half the voltage.