veryconfused

Agricultural
Jul 15, 2021
25
Firstly, I have no idea if I am posting this question in the correct forum, hopefully it's correct. Secondly, I am not an engineer in anyway. I have an issue with EMI from a 3 phase 480v VFD affecting a shielded temperature probe and was hoping somebody on the forum might be able to offer some advice on how to solve my issue.

If I leave the temp probe hanging in the air then the EMI has no affect on the temperature reading. However, as soon as I put the temp probe into the water I start getting temperature spikes. If I only needed to measure the air temp things would be fine, sadly this is not the case.

Does anybody have any ideas on how I might fix this issue? I have ordered some ferrite rings to install on the output side of the VFD. Also, I tried placing a small metal rod in the sump and grounding it with a wire but that hasn't helped.

Any help/advice would be greatly appreciated.

You can see the red temp probe in this image
IMG_4015_uzix9o.jpg

Position of VFD relative to temp probe
IMG_4016_er4avf.jpg

Graph showing temp probe in and out of the water.
Temp_probe_graph_hvcigx.png
 
Replies continue below

Recommended for you

One tank, one pump motor that need shaft grounding. Nothing moves from location to location because it is location specific. Nothing goes bad when the VFD isn't running because the VFD produces the noise that gets coupled onto the shaft and into the pump. Nothing about a grounded phase, all about induced noise. The most obvious cause of the problem (if it isn't direct contact with salt water) has not yet been addressed.

I’ll see your silver lining and raise you two black clouds. - Protection Operations
 
Itsmoke said:
Red; I hope you're not inferring that if a couple of earlier probes haven't leaked yet that means a couple of later ones won't?
No I don't. ;-)
Changing identical units when one has a problem and another has not, is a common way of troubleshooting complex units or units that can not be checked in another way at least where I work.
If the unit that doesn't "work" starts working and vice vers, I would say with 99,9% certainty it isn't the unit.
If I can not find another fault I would go back and look at 0,1% that was left.
I have been doing this so long, so I know the most unlikely things can happen, sooner or later. ;-)

/A


“Logic will get you from A to Z; imagination will get you everywhere.“
Albert Einstein
 
davidbeach said:
Nothing about a grounded phase,
Not sure what you mean here. [ponder]

/A

“Logic will get you from A to Z; imagination will get you everywhere.“
Albert Einstein
 
itsmoked said:
Hi Pete; No worries, I wasn't targeting you. I ran aquariums for nearly 50 years and have seen so many electrical connection to the water over that time it was ridiculous. Almost every "Waterproof" thing wasn't at some point. I'm always leery of water with electrical apparatus associated with it. I was talking instrumentation while thinking safety at the same time.

Thanks. I know you are one of the most laid back and knowledgeable folks here. I overreacted a little. That’s good advice.

itsmoked said:
> There is no good reason for the brine to have enough VFD related electrical noise in it to screw up the data logging unless it's galvanically connected to the power somehow. Furthermore the probe shouldn't be caring unless it's also galvanically connected, i.e. wet to it's insides.

I’m on the same page as you that the probe design (not stated as immersible) and installation (including cable under water) is a huge cause for suspecting a water problem a priori. But I’m also on the same page as redsnake who pointed out: anomaly doesn’t occur in other tanks, anomaly seems to have occurred for multiple probes in this tank, anomaly stops when the vfd stops, anomaly stops when probe lifted. Clearly it's not soley attributable to water intrusion. I think maybe (?) you're suggesting the anomaly is partially attributable to water intrusion but only in combination with vfd noise. Meh, that would require that the water enters enough to disrupt the reading in presence of vfd noise but somehow not enough water inside the probe to cause any problem when vfd is off. I don't 100% rule out water ingress might play a role in that way, but there are way more plausible scenarios to me. Which leads to... I'm on the same page as davidbeach who suggest we focus on High Frequency (HF) voltage coupled into rotor (except I’d go a step further to include HF voltage on stator frame conducted to pump casing, in presence of the possible imperfect stator frame grounding that you had first mentioned... remembering that establishing a good bond to ground can be trickier for HF than for power frequency).

My thinking is that capacitive coupling allows that ac voltage (particularly HF) to jump across the motor airgap without any galvanic connection, and in a similar way it can allow HF to jump across the probe insulation, regardless of whether it is wet or not. That doesn't mean the whole journey is capacitive, the portion of the journey between the pump and the outside of the probe/cable insulation is resistive. The lack of grounded components in the pipe or tank means that any voltage at the pump extends much further through that conducting salt solution before the voltage decays ... so it can more easily get to the probe. Once it gets to the probe, shielding with a ground plane is the best defense against capacitive coupling, but it’s not clear exactly how much/effective shielding we have in this probe and cable. After all that, I think I come to one of the same solutions as you recommended (but for different reasons): We should lift the probe high enough to get that cord out of the water. I would recommend that in general regardless of symptoms, but in regard to solving this particular problem it removes the possibility that interference is transmitted to the underwater portion of the cable through the conductive water. Sure there may also be interference channels that might reach that portion of the cable in air, but those don’t particularly change when we lift the probe out of the water (where the problem went away), and they are harder to fix than simply moving them out of the water (although I wouldn’t mind minimizing the length of exposed cable by extending the conduit as close as possible to the probe... and take the opportunity to ensure there is minimum excess exposed cable length by creating enough conduit length to cover all the cable, or pulling excess cable back inside the conduit if practical, or tucking excess cable back inside if can be done without excessive bending).

That's a lot of general discussion, not much for op unless he wants to understand why we're making some of these recommendations. In terms of practical actions I'd still support voltage check; then either try the glass of fresh water, or else lift probe higher so cable interface is out of water.

I have no doubt things like shaft grounding or alternate probe might possibly end up being the more elegant solution. But we're at the beginning stages, try the above easy few things out first. op does not seem to be in a position to put in place any big changes.

=====================================
(2B)+(2B)' ?
 
I know it's been a while but I thought I would update you all with the solution.

I installed a toroid ring on the output lines on the VFD. This fixed the issue of the noise affecting the temp probe.

Thanks for all your input!
 
[thumbsup2]

“Logic will get you from A to Z; imagination will get you everywhere.“
Albert Einstein
 
It may help some more if you twist the 3 leads together to minimize the loop area between the conductors.
 
Something I didn't think to ask but your picture makes me think I see the problem - Is the VFD to motor cable a proper shielded VFD cable? Are the wires at least in a metal conduit?
 