Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations cowski on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Eurocode 8 Seismic loads on horiz vessel saddles

Status
Not open for further replies.

pvengineer

Mechanical
Jan 6, 2003
6
I have read and read eurocode 8 EN1998-1 seismic loads sections 2 to 4 and cannot seem to determine factors to use for a saddle supported vessel.
 
Replies continue below

Recommended for you

I not familiar with the Eurocode mentioned in your OP. The way that I would analyze the forces on the pier saddles or craddles as follows: estimate the seismic acceleration for the region where the tank is to be located and from which you can calculate the convective and impulsive loads of content within the tank. Half of these loads will transfer thru the centroid of each pier craddle in the form of shear and external moments. From these values you can calculate the pier sizes and if of concrete determine the amount of rebar. Load and moment transfer from pier to footing will be done by using bent dowels or rebar. Footing size and amount of rebar will also be based on base prep details, external loads and moments that act at the saddles of the
piers. Bednar Pressure Vessel Design" as a section but for vertical tanks.
 

"Simple Procedure for Seismic Analysis of Liquid-Storage Tanks" is an internet article based on the Eurocode 8 that you mentioned, however, it is an evaluation for vertical tanks.
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor