My apologies for not getting back to this, sudden heat wave (by our standards) and scramble on A/C as well other projects.
I appreciate the thoughts on this.
I am trying to understand any dynamics of the tank performance at low levels.
There is not intent to try to correct anything. .
I may have mixed things up as to what the question is. What I need to know is what happens as the water level gets down to and then below the Anti Vortex plate (if that is possible or if its just an unknown).
More specifically at what point with our setup at what point do we loose suction?. Its a vertical penetration through the bottom of the tank as follows.
Intake: 26 inches above the bottom of the tank. It has a bell on the end of the intake that goes from 30 inches to 39”. The bell occurs inside the tank in a length of 20 inches)
Anti Vortex Plate: 46 inches above the bottom of the tank. Picture a steel table with 4 legs that sits over the top of the intake. Not attached to the inlet.
20 inches of space between the Anti Vortex plate and the intake mouth.
I tried to follow the links to Gould info and they are broken. Have not been able to follow Goulds lit links through and find the right information. Would you have the direct link?
I don't know how to post a sketch and have limited resources in that regard as far as computer tools go. Give me a number and I can fax one. The link describes our setup as the second option in 2.12.1.6 . i.e bottom entry with intake vertical in the bottom of a tank)
(
Standard cylinder water tank (not on its side). Suction line goes straight down 12 feet from the tank and maintains that over to the pump house as we can get –20F here. Freezing is a given and that avoids the issue (possibly as some loss of tank volume).
Not first choice for Anti Vortex but listed as allowed and for our climate it makes sense (no heating systems to fail as freeze protected by depth of burial).
note: Overflow is a vertical tube in that tank that also goes through the bottom of the tank as well and then into the storm drain system for the same freezing reason. Otherwise we would have to protect piping from freezing and having everything go through the bottom of the tank avoids that (I think it’s the right approach as there is zero maint and monitoring with it and we have enough problems already)
We do keep the tank topped up as much as possible keeping in mind its an auto refill and the control valve drifts a bit. The nominal tank sizing gives us ½ ft lee way below the overflow.
And I am going off topic in responding to the following. Call it a severe disagreement between the maintainers and the committees that dictate the details. They don’t have to maintain it let alone pay for the consequences of what they cause.
Code:
I would not expect an engine driven fire water pump to fly apart on loss of cooling. The engine may eventually seize up. But I see no reason why the pump or coupler would fly apart. The fire is likely the greatest risk. Run the engine to destruction and then buy a new engine.
As mechanics, our entire existence is based on taking care of equipment. This is a case where we are told to let equipment self destruct let alone knowing that its for no purpose. A detached committed can put out an edict, but when your life is spent dedicated to doing just the opposite its not only difficult, it makes absolutely no sense with multiple pumps that have redundancy.
And unless trained and then drilled in, most people are going to try to save a piece of equipment as they are not thinking about their personal risk. That’s part of what I am working on is to get that established.
As a former care taker of the facility as well as the engineer now, I am obligated to ask the questions:
1 do we want to destroy an engine accidentally if there is a failure on the cooling system?
2. Can we prevent it? (we could destroy an engine testing for nor purpose as well)
3. Is there provision in the code to accommodate a situation where engine specific shutdown can be done when you have redundant pumps?
4. If engines are going to self destruct, what do I need to do to ensure the safety of the mechanics (or others) who have responded to the Pumphouse?
Most people have seen a vehicle with a blown radiator stranded by the side of the road. What happens is on loss of cooling (typical a broken fan belt ) the cooling system blows through the radiator cap causing that big cloud of steam. Engine is idled immediatly as the driver pulls off.
Engine is isolated form the occupants and the worst you get is nasty odor of anti freeze.
I know what happens when oil pressure fails, both at idle and under speed. Idle the engine stops, at speed the bearings spin and then things come out the side of the block.
Most people do not know most heavy duty diesels instead of a bore have sleeve inserted in the block sealed at the top and bottom with an O ring. That sleeve is relatively thin and its surrounded by the coolant. The coolant is going to overheat extremely quickly. Typically you have 30 seconds after a coolant failure before the engine destructs if under load.
Factors:
1. In this case, the load disappears (no water in the pump casing)
2. Various Overspeed, undershoot and recovery as the governor attempts to maintain 2100 rpm, so the engine is still at high speed and governor will keep adding fuel to maintain that speed.
3. Massive amounts of torque available as well as 500 hp or better.
4. Inertia from the rotating mass of the impeller/shaft assembly
5. Diesel engine with loss of coolant at speed and under load will seize in 30 seconds.
6. The heat exchanger immediately has no cooling. The closest vehicle analog is a fan (serpentine) belt failure)
7. Spewing of exploding coolant around can get into two intakes (its own intake and adjacent engine) and potentially hydro cylinders.
Initially there will be a steam explosion. Scalding and third degree burns if the fluid hits you. That is an incredibly serious amount of energy being released.
Actually engine failure I do not know. It may seize or it may mechanically self destruct.
If it can rip the rings apart and not seize up, it will continue to run until things come out the side of the block.
Also in play is the coupler and the dynamics of the engine and the rotating mass of the impeller. The mass will assist the engine in maintaining rotation if it does start to seize and the whole thing may have a coupling failure of its own.
Regardless, you do not want to be anywhere close to the engines when the failure occurs.
NFPA can be very intellectually detached as they are not in the room, but there are consequence beyond just the engine stopping. One of the ones I was called in on afterwards also caught fire. That and the others throw stuff around the room or engine compartment (connecting rod failure).
Supposedly the main goal is life safety followed by property protection. My take is that life safety also includes the pump house and safety of the mechanics who are tasked with responding. As the main looses suction its going to be a string of six steam explosions followed by a destroyed engine failure.
Even the redundant pumps will go as loss of main pressure then triggers them to run despite the fact there is no water to fight a fire with anymore. As they would have less load (no water to start with) it would probably take them longer.
My experience with NFPA is that they have become fixated on single fire pump situations and applied that to multiple fire pump situation and a lack of understanding in general of engine driven fire pumps (they are a small minority of the installed systems).
In this case with redundant pumps and their own sensing, there would be no reason not to shut an engine down. There would be no common point of failure as each engine has its own temperature (and oil pressure sensing). Overheat is going to destroy the engine and potentially impact the entire system at no benefit. A dead or even damaged engine is not going to be able fight a fire.
And the fact that they have over-speed protection shutdown (not just blow-off valve) shows that there is some recognition that if it endangers the system you not only can but are actually mandated to shut it down. They recognize the hydraulic implications but not the engine related ones.
These should be treated as systems, not individual components that happen to be put together and a thorough understanding of all the components is required, an engine is not an electric motor.
In this case of multiple pumps with redundancy, an individual pump shutdown on a fault would be safer both to people as well as the best possible insurance that the system as a whole would continue to provide the structural protection its intended to.
While much rarer, oil pressure loss is guaranteed to be worse. In that case the bearings spin, the rods break off the crank and or the pistons wrist pins and those parts will go out the side of the engine.
It really exists a basic lack of understanding of engines when assembled with fire pumps (some very good sprinkler system engineers I have worked with did not have a clue on how engines work and the implications). Great answers on the hydraulic and huh on the engine.