engjg
Structural
- Jan 2, 2015
- 92
I have a flat plate conventionally reinforced concrete slab roof. Contractor wants to use a sand cement slopped topping with either a torch down or liquid applied roof covering.
I am pondering the following about this:
1. I can account for an average or max additional dead load for the varying thickness sloped topping in my design, but if this topping behaves "adhered" is it necessary to consider how will it affect my plate stiffness and design analysis?
2. Project has extreme wind uplift requirements qh ult = 60 psf (ASCE 7-16) regardless of what GCp or GCpi you select or whether you are looking at 0.6xD or not it seems to me that unless adhesion can be technically substantiated the need to specify a significant minimum thickness will exist?
I am pondering the following about this:
1. I can account for an average or max additional dead load for the varying thickness sloped topping in my design, but if this topping behaves "adhered" is it necessary to consider how will it affect my plate stiffness and design analysis?
2. Project has extreme wind uplift requirements qh ult = 60 psf (ASCE 7-16) regardless of what GCp or GCpi you select or whether you are looking at 0.6xD or not it seems to me that unless adhesion can be technically substantiated the need to specify a significant minimum thickness will exist?