I do not have much experience with the FM Global building requirements and I have a project where it popped up at the last minute and I am now trying to ply catchup. I am trying to replicate the values in FM Global Data Sheet 1-28 table 3 (attached). I don't know if I am doing this wrong or not, but looking at my calculations which used ASCE7-05 and the numbers given in the table which are suppose to use ASCE7-05 and they don't match.
For example, given exposure C, V=100mph, H=30ft I calculate a wind pressure of 25.1 psf while FM calculates a wind pressure of 29psf. I know FM is suppose to yield higher uplifts, but they seem to specifically reference ASCE 7 and I am wondering why my numbers do not match.
Amy insight would be appreciated.
For example, given exposure C, V=100mph, H=30ft I calculate a wind pressure of 25.1 psf while FM calculates a wind pressure of 29psf. I know FM is suppose to yield higher uplifts, but they seem to specifically reference ASCE 7 and I am wondering why my numbers do not match.
Amy insight would be appreciated.