Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations cowski on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Glulam Cable Truss

Status
Not open for further replies.

MIStructE_IRE

Structural
Sep 23, 2018
816
Hi,

An architect I’m working with is looking to span a sports hall roof with large double Glulam beams with a Macalloy tension member below, creating a very simple truss. There will be a single vertical element at midspan very similar to the attached photo (only I don’t have the glulam arch above).

He doesn’t want anything tying the bottom chords of the truss together and I have no uplift case here as the roof is more than heavy enough.

My question is, since I can’t tie the bottom chords together, meaning that I can’t tie the midspan struts together (much like the photo) should the strut be designed as a mini cantilever with fixity to the top glulam chords? I have a feeling it may try to whip laterally otherwise..

Any thoughts?
 
 https://files.engineering.com/getfile.aspx?folder=02081aed-9e15-4e5d-b1e4-6f8134fe91b4&file=210ACF20-EA35-4C04-BA32-843132593229.png
Replies continue below

Recommended for you

Yes, the vertical strut would need some restraint, cantilevering it seems like the logical answer. You'd just need to be careful about the fixity at the top, would you have members perpendicular at top chord to take out the twist of the Glulam rafter on which the fixity relies?
 
Thanks! Yes, I will have them anyway to fully restrain this chord. I’m thinking of the strut being a tapered cruciform. The crucifix representative of what I’m doing to myself on these jobs!!
 
Just be aware that cruciforms have another torsional/twisting buckling mode under axial loads that might need to be investigated. Here's some background information on this aspect.
 
Great resource! It will likely end yp as a flanged cruciform. At 8m overhead the flanges won’t even be noticeable!
 
MIStructE IRE:
Check out this thread - thread507-124363


Check out Eng-Tips Forum's Policies here: