I need some help here. I have the SMACNA HVAC duct construction standards book open in front of me. I am designing a 72" X 43" supply duct with a 3" in. wg static pressure and 29400 CFM. I would like to determine the appropriate sheet metal gauge to use for this application but I am not really sure what to do Table 1-6 in the booklet does not have anything beyond circular diameter of 24". Any guidance would be appreciated.

 
Replies continue below

Recommended for you

could you look a little more into tables?

i don't have whole smacna book, but i do have table excerpts, and in some of my tables 28" is smallest dimension, while largest one is " over 96" "

be sure to make difference between true circular ducts and equivalent diameters of rectangular ducts, as the tables are not interchangeable, stiffness and construction are different.
 
Without seeing the application, It sounds like your duct is oversized for that flow. This is what we would build - 56.25” length with TDC both ends, gauge = 22 all sides, small pits, seal all seams, 1.5x1.5x1.5 intermediate reinforcing at mid span of the 56.25” only on 72” sides. Two (2) condu-loc tie rods 1” in from both ends in the center of the 72 span. Hang at 9’-6” intervals wrod/angle or gripple. I believe this meets the latest designs and should be the best value.
 
72x43? I would go with at 60x36 if you can. That is only .1"/100ft drop at that flow and 2250 fpm. And why the 43? When the next guy goes to measure the duct when it's insulated he's going to call it a 42 or 44, so why not stick to regular sizes.
 