Hey guys,
At a job we are doing here in NY, I have come across something that is unusual to me. Here is the situation.
We are constructing a new building here and the loads for the cooling system dont seem to add up in the following two ways. I personally have never done a cooling calculation for an entire building but using these simple common sense methods, things arent adding up.
- The building is approximately 700,000 square feet. If you do 10 watts per square foot, I came out to just under 2000 tons of cooling. Which makes sense because the building has three 1000 ton trane chillers (with one as a spare)
from here is where it gets funny,
each chiller needs 1700 gpm of evaporator flow. However they have not speced 3 chilled water pumps, but 4 chilled water pumps. Each with a flow rate of 1700 gpm. You would think that if 2 chillers are required you would provide 1 pump for each chiller, yet they call for 4.
- If you add up the total amount of chilled water required for the air handlers in the building you get about 8500 gpm. If you use an 80% diversity, you get about 6650 gpm required. All of the piping in the building is designed for about 6650 gpm.
I would think that the amount of water flow for the air handlers should add up to the approximate load for the square footage of the building. Am I incorrect here?
Either 1 of the two following scenarions
They are either short 1 chiller
or
They have hugely oversized the piping and air handlers.
I have never heard of a building have a load like that is so high before.
I dont think it should make any difference but the building is set up for variable flow primary cooling.
Please let me know what you guys thing. Again I am a third party casual observer, but to me something doesnt look right in the design.
Any help is appreciated.
At a job we are doing here in NY, I have come across something that is unusual to me. Here is the situation.
We are constructing a new building here and the loads for the cooling system dont seem to add up in the following two ways. I personally have never done a cooling calculation for an entire building but using these simple common sense methods, things arent adding up.
- The building is approximately 700,000 square feet. If you do 10 watts per square foot, I came out to just under 2000 tons of cooling. Which makes sense because the building has three 1000 ton trane chillers (with one as a spare)
from here is where it gets funny,
each chiller needs 1700 gpm of evaporator flow. However they have not speced 3 chilled water pumps, but 4 chilled water pumps. Each with a flow rate of 1700 gpm. You would think that if 2 chillers are required you would provide 1 pump for each chiller, yet they call for 4.
- If you add up the total amount of chilled water required for the air handlers in the building you get about 8500 gpm. If you use an 80% diversity, you get about 6650 gpm required. All of the piping in the building is designed for about 6650 gpm.
I would think that the amount of water flow for the air handlers should add up to the approximate load for the square footage of the building. Am I incorrect here?
Either 1 of the two following scenarions
They are either short 1 chiller
or
They have hugely oversized the piping and air handlers.
I have never heard of a building have a load like that is so high before.
I dont think it should make any difference but the building is set up for variable flow primary cooling.
Please let me know what you guys thing. Again I am a third party casual observer, but to me something doesnt look right in the design.
Any help is appreciated.