Deutero

Specifier/Regulator
Jul 20, 2006
44
0
0
US
3/4" dia ladders rungs, 3/16 fillet welded all around, each end, to flat bar 3/8 x 3 stringers. The rungs do not penetrate the stringers.

Are the supports a fixed or pinned connection?

Thank you ...
 
Replies continue below

Recommended for you

JAE and UcfSE are correct here.

This is like an I-shaped beam terminating into, and welded to, an I-shaped support "girder" (beams at 90 degrees to each other). Because the support girder, being I-shaped, has small torsional stiffness, the reaction delivered to it by the beam will be a vertical force, with little or no moment. All the connection stiffening in the world won't change that. Replace the I-shaped girder with a closed tubular shape and the connection now has the potential to transfer moment in addition to the vertical force.
 