Friends:
I'm just the CAD guy at a panel-builder, but am often required to size CBs and fuses to satisfy specs written by real engineers. We're to build a panel for a duplex submersible sewage pump station with 20hp (27FLA) Flygt pumps and Toshiba TE-39 (19-39A) soft starters. The engineer's spec calls for motor circuit protectors, and the customer wants a UL label, so I'm also using current-limiting fuses (class J) on each starter for a higher SCCR. Plus we'll have a circuit breaker to disconnect the panel.
The MCP rated for 30A has a trip setting for 27 FLA at 300A, even though with a soft starter the inrush can be programmed to 200%-300% of FLA. I want to use 60A fuses on each starter and a 60A main breaker (the ultrasonic controller will prevent simultaneous starting), but having all these different sizes looks incongruous and could be difficult to justify. Unfortunately, the obvious remedy - no MCPs - is not available. Is my sizing too small, or too large, or both at once? Thanx!
I'm just the CAD guy at a panel-builder, but am often required to size CBs and fuses to satisfy specs written by real engineers. We're to build a panel for a duplex submersible sewage pump station with 20hp (27FLA) Flygt pumps and Toshiba TE-39 (19-39A) soft starters. The engineer's spec calls for motor circuit protectors, and the customer wants a UL label, so I'm also using current-limiting fuses (class J) on each starter for a higher SCCR. Plus we'll have a circuit breaker to disconnect the panel.
The MCP rated for 30A has a trip setting for 27 FLA at 300A, even though with a soft starter the inrush can be programmed to 200%-300% of FLA. I want to use 60A fuses on each starter and a 60A main breaker (the ultrasonic controller will prevent simultaneous starting), but having all these different sizes looks incongruous and could be difficult to justify. Unfortunately, the obvious remedy - no MCPs - is not available. Is my sizing too small, or too large, or both at once? Thanx!